    What MCB's under the new 17th Ed regs?

    Hi,

    I wonder if a fellow sparky can help with a query re: 17th Edition regulations..

    what MCB should be used for:
    • Washing Machine
    • Fridge Freezer


    ie 16A or 32A

    please advise
  • maarksparky
    Member
    • Jun 2008
    • 88

    #2
    any thoughts guys??

    btw, both have thier dedicated circuits on 2.5mm2 wire

    thanks

    Comment

    • lagerland
      V.I.P. Member
      • Sep 2010
      • 6031

      #3
      16 a for a radial circuit 32a on the ring main linked to an rcd mate.......................
      I know you believe you understand what you think i said



      >>>>>>>>>>>>>>>> BUT <<<<<<<<<<<<<<<<
      I am not sure you realise that what you heard is not what i meant ! sigpic

      Comment

      • maarksparky
        Member
        • Jun 2008
        • 88

        #4
        Originally posted by lagerland
        16 a for a radial circuit 32a on the ring main linked to an rcd mate.......................
        cheers mate,

        so in essence, I should use 16A MCB for both Fridge Freezer and Washing Machine dedicated radial circuits?

        Comment

        • lagerland
          V.I.P. Member
          • Sep 2010
          • 6031

          #5
          Originally posted by maarksparky
          cheers mate,

          so in essence, I should use 16A MCB for both Fridge Freezer and Washing Machine dedicated radial circuits?
          Yes mate...........